--- title: "Recipe Group" --- # Recipe Group > You can use Standard or Block Transaction Groups to create recipe management system with bi-directional communication to pass database information to the PLC when requested. The main advantage of using transaction groups to design the recipe management group is that the group will write to all the OPC locations. ### To use transaction groups to create recipes 1. Create a new **Standard** transaction group. 2. Drag a set of tags into the group's **Basic OPC/Group Items**. One of these tags should be a recipe index tag and needs to be read-only. 3. Change the recipe index tag to read-only by selecting **Read-only** from the drop-down in the **Target Name** column. 4. Go to the **Action** tab, and set the following: * **Update mode**: choose **OPC to DB**. * **Table name**: select the table name that contains the recipes. This table should have an index. * **Use custom index column**: select the check box and choose the column that is the index from the table. * **Store timestamp to a column**: deselect the check box. 5. In the **Table action** area of the **Action** tab, click **update/select** and **custom** to create a custom clause that references the read-only tag. The read-only tag and the name of the index column of the database must be the same. Do not include the word "where" because it is assumed to be part of the enclosed statement. 6. Click **Enable** to enable the group and save the project to start the transaction group. 7. Test the recipe group by entering a new value into the recipe number (for example, the tag that is mapped to the index of the recipe database). The recipe values will download to the appropriate tags.
